nickelec

Senior Member
Location
US
Need some help figuring out a feeder size for 200 40a Electric ranges

Sent from my SM-G965U using Tapatalk
 
Have you looked at Table 220.55 and it's notes?

Roger
 
You can use column C without knowing the kW. Since this is 3 phase you need to find the maximum number of ranges connected to any one phase. Multiply that number by 2 and use that as the total number of ranges.
 