A discussion came up concerning supplying power to a range hood. My understanding is as follows (Based on '17 NEC):
1.422.16(B)(4) allows the range hood to be cord & plug connected if all the stipulations of that Section are met including an individual circuit.
2. You can not cord and plug connect the range hood unless it is supplied by an individual circuit as required by 422.16
3 If you hard wire the range hood it can not be connected to the small appliance branch circuit as 210.52(B) prohibits other "outlets" to be connected to the S/A circuit.
4.The range hood can be hardwired to a general lighting circuit as long as it does not violate 210.23
Is there a flaw in the above statement ??
1.422.16(B)(4) allows the range hood to be cord & plug connected if all the stipulations of that Section are met including an individual circuit.
2. You can not cord and plug connect the range hood unless it is supplied by an individual circuit as required by 422.16
3 If you hard wire the range hood it can not be connected to the small appliance branch circuit as 210.52(B) prohibits other "outlets" to be connected to the S/A circuit.
4.The range hood can be hardwired to a general lighting circuit as long as it does not violate 210.23
Is there a flaw in the above statement ??