JonnnyDonuts
Member
- Location
- New York
- Occupation
- Engineer
I am currently working on a project where we are replacing a 480V 1200A distribution switchboard filled with fused switches (installed in the 80s) with a 1200A distribution panelboard with circuit breakers. The panelboard is serving mechanical loads which were also installed in the 80s.
This replacement panelboard will have a 600A CB, a 400A CB, and 5 30A CBs.
However, another engineer told me that it would be risky to design a panelboard like this. He said the inrush current from the large loads would damage the smaller mechanical units on the same panelboard and recommended installing a subpanel to handle the 30A CBs.
Is this true? I've seen plenty of panelboards where a 400A CB and a 15A CB are on the same 480V panelboard bus, especially in labs; and this is without any electronic breaker adjustments. I don't mind making the change, I just want to know what the right way to go about this is.
This replacement panelboard will have a 600A CB, a 400A CB, and 5 30A CBs.
However, another engineer told me that it would be risky to design a panelboard like this. He said the inrush current from the large loads would damage the smaller mechanical units on the same panelboard and recommended installing a subpanel to handle the 30A CBs.
Is this true? I've seen plenty of panelboards where a 400A CB and a 15A CB are on the same 480V panelboard bus, especially in labs; and this is without any electronic breaker adjustments. I don't mind making the change, I just want to know what the right way to go about this is.