Can I get a ruling on this conclusion I've come to regarding a range/cooktop calculation?
So, I have 8-3 NM cable supplying a J-box with 2 appliances served by each of those circuits, a built-in(wall-mount?) oven and a cooktop. The oven is rated at 8700w and the cooktop at 4200w. I am wanting to verify that this size wire is legal....with reference to Table 220.55 in NEC 2011 "Demand Factors and Loads for.....and other household cooking appliances over 1-3/4 kW rating (Column C to be used in all cases except as otherwise permitted in Note 3).
So, 4200+8700/240 = 53.75a. Now, I figure I use row 2, for 2 appliances, and use Column C. If 65% of 53.75 = 34.9375a, is size 8 AWG sufficient for these loads and satisfy code? Or does the 80% capacity rule apply here?
Thank you in advance for your thoughts.
Kevin
So, I have 8-3 NM cable supplying a J-box with 2 appliances served by each of those circuits, a built-in(wall-mount?) oven and a cooktop. The oven is rated at 8700w and the cooktop at 4200w. I am wanting to verify that this size wire is legal....with reference to Table 220.55 in NEC 2011 "Demand Factors and Loads for.....and other household cooking appliances over 1-3/4 kW rating (Column C to be used in all cases except as otherwise permitted in Note 3).