Re: range powering affected phase leg?
I don't think we are seeing the same picture in our respective minds. Try drawing a picture as follows:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Draw 3 vertical lines, representing wires coming from the meter. Label them A, B, N.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Draw a symbol for the main breaker on "A" and "B." Continue the lines downward to represent the two bus bars. Terminate the line for "N" on a box to represent the neutral bar.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Let's say "A" was the "good phase," and "B" was the phase with the bad connection at the main breaker.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Draw a symbol for a 2-pole breaker to take power from both A and B, and draw horizontal lines over to a box to represent the range.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Draw a symbol for a 1-pole breaker to take power from B. Draw a horizontal line over to a circle to represent a light. From the other side of the circle, draw a horizontal line back to the neutral bus.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">Under normal circumstances (i.e., no bad connection), with the range turned on, current will flow from the meter, through the main breaker, along phase "A" to the range, back to "B," back through the main breaker, and back to the meter. At the same time, with the light switch turned on, current will flow from the meter, through the main breaker, along phase "B" to the light, along the neutral wire to the neutral bus, and back out (not going through the main breaker) to the meter.
Now let's talk about the bad connection. Turn off the range, and make sure the light switch is on. Just as in the "normal circumstances," current will flow from "B" to the light and back to "N." However, with the bad connection, the resistance will be high, and the current will be low. There will be current through the light bulb, but it will not be enough current to cause the lamp to glow brightly enough for the human eye to notice.
Now turn on the range. There will be both the current paths described above. The current paths do not change. There will be current flowing from "A" to the range and back to "B." There will be current flowing from "B" to the light and back to neutral. The difference is that the current from the range will overcome the resistance of the bad connection. That will permit more current to flow through the "not so bad anymore" connection through the light, and you will be able to see the lamp glowing normally.