Calculate the minimum loads which will be used for sizing the feeders supplying the following 240 volt household ranges:

one 16.8 kw range
______________________________________________________
one range in column c = 8kw
16.8 kw-12 (Note 1 T 220.55)= 4.8
4.8 x 1.05= 5.04 kw
5.04+8= 13.04 kw

Answer Key says 10 kw ?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Calculate the minimum loads which will be used for sizing the feeders supplying the following 240 volt household ranges:

one 16.8 kw range
______________________________________________________
one range in column c = 8kw
16.8 kw-12 (Note 1 T 220.55)= 4.8
4.8 x 1.05= 5.04 kw
5.04+8= 13.04 kw

Answer Key says 10 kw ?


Re-check the red portion of your calculation.
 

Carlos G

Member
Range question

Range question

1 range col C= 8Kw

16.8Kw-12=4.8 Kw x 5% for each kw over 12= 24 %

So, 8Kw x 1.24= 9.92----10kw
 

Jim Shorts

Member
Location
Central Florida
8 kw + 25% = 10 kw

.8 is a major fraction of 1 so you must look at this as a 17 kw range.
17 exceeds 12 by 5 so you must increase column c by 25% (5 x 5 = 25)
 