Does a Range require AFCI or GFCI per 2020 Nec. I haven't done a range in a while. I dont have my code book with me

Thanks
 
Is range a 120V or 240V? All 120V 15A and 20A in a kitchen need AFCI. If 240V, if 120V to ground it might need GFCI regardless of proximity to the sink unless tocal or state has adopted a TIA
 
Just curious as to what others are doing when code requires GFCI protection and you cant find a GFCI breaker in GE
 
Would the answer not be dependent on dwelling unit vs non-dwelling unit ??

This is from the 2020
(A) Dwelling Units.

All 125-volt through 250-volt receptacles installed in the locations specified in 210.8(A)(1) through (A)⁠(11) and supplied by single-phase branch circuits rated 150 volts or less to ground shall have ground-fault circuit-interrupter protection for personnel.


Other Than Dwelling Units.

All 125-volt through 250-volt receptacles supplied by single-phase branch circuits rated 150 volts or less to ground, 50 amperes or less, and all receptacles supplied by three-phase branch circuits rated 150 volts or less to ground, 100 amperes or less, installed in the locations specified in 210.8(B)(1) through (B)(12) shall have ground-fault circuit-interrupter protection for personnel.

This covers the hvac outdoors
(F) Outdoor Outlets.

All outdoor outlets for dwellings, other than those covered in 210.8(A)(3), Exception to (3), that are supplied by single-phase branch circuits rated 150 volts to ground or less, 50 amperes or less, shall have ground-fault circuit-interrupter protection for personnel.
Exception No. 1:
Ground-fault circuit-interrupter protection shall not be required on lighting outlets other than those covered in 210.8(C).
Exception No. 2:
Ground-fault circuit-interrupter protection shall not be required for listed HVAC equipment. This exception shall expire September 1, 2026.
 