what is the equivalent 3 phase demand load in va for 10 - 11kw household electric ranges installed in an apartment complex supplied by a 120\208v, 3 phase, 4 wire system
a. 23,400
b. 30,500
c. 34,500
d. 38,200
220.55 coulum c says 23, at least thats the answer as I see it. So, is a. a good answer? Is this why they state "equivalent"? Or, am I doing this wrong?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I believe the answer is C) 34,500VA

There are 4 units max between any two phases, which means figure 8 units. The demand for 8 units is 23kW per T220.55, or 11.5kW per phase.

The "equivalent three phase" load would be 11.5kW per phase * 3 phases =34.5kW.
 