Ranges

Status
Not open for further replies.

tbooth

New member
I find that most ovens/ranges are connected with two ungrounded conductors and ground.
But most have a clock or timer or digital temp display which to me indicates nuetral load. The cord supplied only has 3 conductors. This does not seem right.
Is this addressed in the code?
 
Keep in mind manufactures may also design these digital displays with a 240v power supply. Thus not needing a neutral. From an engineering standpoint this would make sence and add no aditional cost to production.
 
Keep in mind manufactures may also design these digital displays with a 240v power supply. Thus not needing a neutral. From an engineering standpoint this would make sence and add no aditional cost to production.

Most of those ovens you speak of use a nuetral as a grounding conductor not the uninsulated ground as a grounded conductor. I was understood that if the oven branch circuit originated at the service panel then the Nuetral could serve as the grounding conductor as I remember.

what the mistake was that this was done at a sub panel. Branch circuits were never intended to be wired this way. Then the issue of the uninsulated wire as a nuetral I don't think was ever permissable.

When I change out a Range I alway's add the proper cord and receptacle as per code. Especially if it was never permissable at the time of contruction.
 