Rapid shutdown for system with panels on more than one building

Status
Not open for further replies.

Pelagic13

Member
Location
Maine
Occupation
Installer
Quick question,
When installing a residential system with panels on both a house and a detached garage, is it required by nec 2017 to have disconnecting means for rapid shutdown on both structures? Or would a switch at just the meter main suffice?
Thanks so much for any input here.,
Cory
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
If you are using AC disconnecting to initiate rapid shutdown, and complying with the rest of the code (particularly 225.31), then you'll have initiating devices on each building anyway.
 