Good morning everyone,
This thread intends to be useful for those people more used to working in IEC standards but NEC/CEC newcomers.
Hence I think that it would be useful if you could confirm my approach and please provide the correct NEC/CEC points which defines the matters the best.
On the other hand, please correct whatever you consider necessary.
In IEC the rated voltage at secondary side of transformer is related to the non-load voltage and the rest of equipment downstream (even motors) are voltage rated with the nominal voltage (if you are going to measure with a tester, the measurement should match closely with the rated voltage of the panel).
Voltage drops in % are referred to the nominal voltage or utilization voltage.
In CEC/NEC, transformers and downstream panels are rated with the non-load voltage (if you are going to measure with a tester in a panel, the measurement will be less as it is the utilization voltage, i.e. 575V but panel is 600V).
Motors are rated based on this utilization voltage.
Voltage drops in % are referred to the rated voltage of the system.
Note: the voltage tolerances for system and motors are different in IEC vs NEC/CEC (NEMA/CSA); this is logical since it is related to the differences (IEC vs NEC/CEC) of rated voltage of the systems against their utilization voltages.
Summarizing, please find below example charts of Rated Voltage of the NEC and CEC but "translated" into a IEC understanding.
it is referred to a case of LV but it can be extrapolated.
PoV IEC: From Point of View of IEC, means that if the project had developed in IEC std. Attention: this does not mean compatibility between equipment designed in different standards; only useful to understand the voltage matter.
Hope this can be useful.
Best regards
This thread intends to be useful for those people more used to working in IEC standards but NEC/CEC newcomers.
Hence I think that it would be useful if you could confirm my approach and please provide the correct NEC/CEC points which defines the matters the best.
On the other hand, please correct whatever you consider necessary.
In IEC the rated voltage at secondary side of transformer is related to the non-load voltage and the rest of equipment downstream (even motors) are voltage rated with the nominal voltage (if you are going to measure with a tester, the measurement should match closely with the rated voltage of the panel).
Voltage drops in % are referred to the nominal voltage or utilization voltage.
In CEC/NEC, transformers and downstream panels are rated with the non-load voltage (if you are going to measure with a tester in a panel, the measurement will be less as it is the utilization voltage, i.e. 575V but panel is 600V).
Motors are rated based on this utilization voltage.
Voltage drops in % are referred to the rated voltage of the system.
Note: the voltage tolerances for system and motors are different in IEC vs NEC/CEC (NEMA/CSA); this is logical since it is related to the differences (IEC vs NEC/CEC) of rated voltage of the systems against their utilization voltages.
Summarizing, please find below example charts of Rated Voltage of the NEC and CEC but "translated" into a IEC understanding.
it is referred to a case of LV but it can be extrapolated.
Rated Voltages: | NEC | PoV IEC |
TRAFOS | 4160/480V | 4160/480V |
SYSTEM | 480V | 460V |
PANELS | 480V | 460V |
LOADS | 480V | 460V |
MOTORS | 460V | 460V |
CABLES | 600V | 1000V |
VD% | VD/480V | VD/460V |
TESTER | ±460V | ±460V |
Rated Voltages: | CEC | PoV IEC |
TRAFOS | 4160/600V | 4160/600V |
SYSTEM | 600V | 575V |
PANELS | 600V | 575V |
LOADS | 600V | 575V |
MOTORS | 575V | 575V |
CABLES | 600V | 1000V |
VD% | VD/600V | VD/575V |
TESTER | ±575V | ±575V |
PoV IEC: From Point of View of IEC, means that if the project had developed in IEC std. Attention: this does not mean compatibility between equipment designed in different standards; only useful to understand the voltage matter.
Hope this can be useful.
Best regards