We have a 200A OCPD with 4/0 aluminum feeder to an interior sub panel. The rating of XHHW-2 based on NEC table is 205Amps at 90C. The ahj is rating that cable based on 75C.
Our calculation for load side tap allows us to stay with a 200Amp OCPD and the 4/0 aluminum. However, the ahj is asking to reduce the OCPD to 175A because they are seeing the rating of the cable at 180A based on table and the 75C column.
your thoughts is appreciated.
Do I have a leg to stand on or the ahj does?