Feeding a fire pump directly from the customer owned outdoor pad mounted utility transfomer as the building has a MV service. Per 230.70 & 225.31 a disconnect switch is required to disconnect all ungrounded service conductors that enter the building. NEC 695.4 indicates sizing the OCP for LRC but if I do not have OPC in the switch would the rating of the disconnect switch itself still need to be sized for this? I would prefer to leave the OCP out of the disconnect switch to avoid sizing it for locked rotor current keeping the disconnect switch much smaller because in my case 404.13(B) would apply so I would need to dive further into that
Looking for the section of the code that indicates the disconnect (not the OCP) must be sized for this if it exists. Am I missing something on this?
Thanks!