I’m currently studying for my WV masters. Today I was doing some calculation questions and came across this question.
Determine the MINIMUM size ungrounded (phase) 75degree ALUMINUM service entrance conductors required for a 150ampere service of a one-family dwelling with a 120/240volt ,3wire, single phase electrical system.
table 310.12 give you 2/0 aluminum.
Or 150x83%=125amps. Next size up is 2/0 rated for 135amps.
Simple right, well after the quiz going through checking my answers and this is what I came across for theirs.
150amperes x 83%124.5
*note-size 1/0 AWG aluminum conductors with an ampacity of 125amperes should be selected from table 310.12.
Am I correct in saying they are wrong, because they are applying the 83% to there service rating than using that number (124.5ampere) as there service size selection out of T310.12 to select an even smaller size conductor.
Determine the MINIMUM size ungrounded (phase) 75degree ALUMINUM service entrance conductors required for a 150ampere service of a one-family dwelling with a 120/240volt ,3wire, single phase electrical system.
table 310.12 give you 2/0 aluminum.
Or 150x83%=125amps. Next size up is 2/0 rated for 135amps.
Simple right, well after the quiz going through checking my answers and this is what I came across for theirs.
150amperes x 83%124.5
*note-size 1/0 AWG aluminum conductors with an ampacity of 125amperes should be selected from table 310.12.
Am I correct in saying they are wrong, because they are applying the 83% to there service rating than using that number (124.5ampere) as there service size selection out of T310.12 to select an even smaller size conductor.