Can an RCBO (Residual Current Detection Circuit Breaker) be used when there is no neutral present? All of the big boys (AB, ABB, Schneider) show connection diagrams that monitor leakage current from Line to Neutral.
I have a 220V 3-phase Delta supply without neutral and am required to use an RCBO (ELCB, combo CB & Leakage detect, etc). I am wondering if the device will function in the manner when it is monitoring between Line and ground. I actually doubt it as the device is intended to measure compare the current in (sum of the Lines) and the current out (return through neutral). Any thoughts or experience that you would like to share?
I have a 220V 3-phase Delta supply without neutral and am required to use an RCBO (ELCB, combo CB & Leakage detect, etc). I am wondering if the device will function in the manner when it is monitoring between Line and ground. I actually doubt it as the device is intended to measure compare the current in (sum of the Lines) and the current out (return through neutral). Any thoughts or experience that you would like to share?