Hi,
I've designed power distribution panels in the past, and just slapped the SCCR of my panel onto it and let the facility installing the panel deal with getting the available short circuit current below the SCCR. I'd like to however start with increasing the SCCR on my panels so they can be installed in more locations, however I'm hitting a snag with one particular one that utilizes a 30mA RCD.
I have a design where I have an available fault current of 40kA @480VAC and I have a control panel where I'm distributing this power via some current limiting fuses in the feeder circuit through power distribution blocks down to some UL489 MCB's to a 30mA RCD's that have outlets downstream.
After doing the SCCR calc according to UL508A, I realize this design is flawed since, even though the let thru current of the feeder fuse is less than 10kA, there is a scenario where the RCD or the UL489 MCB will trip before the CL fuse does, which would destroy my RCD and or MCB. After thinking about it a bit more, in case of a phase to ground fault, the RCD would always trip first, since that's set to 30mA, way lower than the 15A for the MCB. This makes me realize that this 10kA RCD can never be used on a circuit where the available fault current on the line side of the feeder exceeds 10kA. Am I missing something here? Any advice would be appreciated. Even if I were to swap out the MCB for a CL fuse, the RCD is still the bottleneck, how do I solve this?
I've designed power distribution panels in the past, and just slapped the SCCR of my panel onto it and let the facility installing the panel deal with getting the available short circuit current below the SCCR. I'd like to however start with increasing the SCCR on my panels so they can be installed in more locations, however I'm hitting a snag with one particular one that utilizes a 30mA RCD.
I have a design where I have an available fault current of 40kA @480VAC and I have a control panel where I'm distributing this power via some current limiting fuses in the feeder circuit through power distribution blocks down to some UL489 MCB's to a 30mA RCD's that have outlets downstream.
After doing the SCCR calc according to UL508A, I realize this design is flawed since, even though the let thru current of the feeder fuse is less than 10kA, there is a scenario where the RCD or the UL489 MCB will trip before the CL fuse does, which would destroy my RCD and or MCB. After thinking about it a bit more, in case of a phase to ground fault, the RCD would always trip first, since that's set to 30mA, way lower than the 15A for the MCB. This makes me realize that this 10kA RCD can never be used on a circuit where the available fault current on the line side of the feeder exceeds 10kA. Am I missing something here? Any advice would be appreciated. Even if I were to swap out the MCB for a CL fuse, the RCD is still the bottleneck, how do I solve this?