RCI vs. GFCI

Status
Not open for further replies.
A UL Class A GFCI is meant to trip between 3 mA and 7 mA. A UL Class B GFCI is meant to trip between 20 mA to 40 mA.

Look at 426.28--This would be one application. They protect equipment not personell.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Do they even make class B gfci's anymore?
Yes, but they are used mainly in machine control systems now, referred to as "Arcing Ground Fault" breakers. In commercial / residential systems, the new requirements for AFCIs (Arcing Fault Circuit Interrupters) have taken over where these used to be used. AFCIs are similar, but more sophisticated in some ways because 1) they don't require that the arc go to ground, and 2) they have to be able to distinguish between a normal "working" arc, such as in a light switch, and one that might cause a fire, i.e. a loose connection.
 