Good Morning Friends, Could someone show/illustrate the calc for this article.
Thanks, Lyle
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Good video, but, IMHO Mike kinda skimmed past the OP's calculation question.
I believe the situation to be as such:
Assume you have a 75 kva 3 phase 480/208Y1220 transformer with a 125 amp primary OCP device.
1/3 of the primary OCP device will be 42 amps.
The transformer ratio 480/208 is 2.31
42 amps X 2.31 is 97 amps so the minimum conductor ampacity would be 97 amps.

(I hope I did that correctly...the ratio throws me sometimes... if I'm wrong someone here will correct me)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Good video, but, IMHO Mike kinda skimmed past the OP's calculation question.
I believe the situation to be as such:
Assume you have a 75 kva 3 phase 480/208Y1220 transformer with a 125 amp primary OCP device.
1/3 of the primary OCP device will be 42 amps.
The transformer ratio 480/208 is 2.31
42 amps X 2.31 is 97 amps so the minimum conductor ampacity would be 97 amps.

Does anyone have an idea why we use this ratio?
 