Aleman
Senior Member
- Location
- Southern Ca, USA
Hey folks here's a question for you.
Per Article 409.104, looking at the 2011 NEC,
409.104 Wiring Space.
(A) General. Industrial control panel enclosures shall not
be used as junction boxes, auxiliary gutters, or raceways for
conductors feeding through or tapping off to other switches
or overcurrent devices or other equipment, unless the conductors
fill less than 40 percent of the cross-sectional area of the
wiring space. In addition, the conductors, splices, and taps
shall not fill the wiring space at any cross section to more than
75 percent of the cross-sectional area of that space.
One of our electricians wants to run a 120VAC circuit through a control panel, in SOOW cable, that is fed from an external source. This will be then routed through to an outlet outside of the panel. Basically using the panel as a raceway. I said no but need to show him why. So when looking at ART 409, as written above...it appears that the reason to NOT use a control panel as a gutter or raceway is space dependent. If looked at from the space dependent point of view, he would be able to run the cable through the panel. I have always been taught that control panels cannot be used as raceways but this is the first time I really read the article. And it looks to present an option to use the panel as a raceway.
Per Article 409.104, looking at the 2011 NEC,
409.104 Wiring Space.
(A) General. Industrial control panel enclosures shall not
be used as junction boxes, auxiliary gutters, or raceways for
conductors feeding through or tapping off to other switches
or overcurrent devices or other equipment, unless the conductors
fill less than 40 percent of the cross-sectional area of the
wiring space. In addition, the conductors, splices, and taps
shall not fill the wiring space at any cross section to more than
75 percent of the cross-sectional area of that space.
One of our electricians wants to run a 120VAC circuit through a control panel, in SOOW cable, that is fed from an external source. This will be then routed through to an outlet outside of the panel. Basically using the panel as a raceway. I said no but need to show him why. So when looking at ART 409, as written above...it appears that the reason to NOT use a control panel as a gutter or raceway is space dependent. If looked at from the space dependent point of view, he would be able to run the cable through the panel. I have always been taught that control panels cannot be used as raceways but this is the first time I really read the article. And it looks to present an option to use the panel as a raceway.