Re-energizing power after a fire

Status
Not open for further replies.

hotrod71

Member
If you have a small fire in an attic that has damaged 2 or 3 circuits and you have disconnected all associated circuits in the service panel, is there a Standard of Care that requires the electrician to test all other non-associated circuits in the home with a meg ohm meter to find preexisting compromised insulation on conductors well outside the fire damaged area on a different floor of the home.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
hotrod71 said:
If you have a small fire in an attic that has damaged 2 or 3 circuits and you have disconnected all associated circuits in the service panel, is there a Standard of Care that requires the electrician to test all other non-associated circuits in the home with a meg ohm meter to find preexisting compromised insulation on conductors well outside the fire damaged area on a different floor of the home.

I have a feeling that someone has told you this is the case and you don't want to do it. Most insurers have a defined T+C that you agree to when you take on this kind of work. I would read what you agreed to first.
 

celtic

Senior Member
Location
NJ
barbeer said:
As an inspector- I require a notarized letter from EC stating that the system has been checked or repaired to alleviate the liability on the AHJ. :smile:

What standard accomplishes "checked "?
 

barbeer

Senior Member
I would think that a properly trained, qualified electrician would have the knowledge and tools to effectively accomplish this task. If you positively need a standard (of which I believe there is not a recognized one) try this one.

NFPA 921: Guide for Fire and Explosion Investigations, 2004 Edition

This should help with what to look for- and this one should help with the correct way to repair what needs to be.

National Electrical Code? 2005 Edition (NFPA 70)
 

celtic

Senior Member
Location
NJ
barbeer said:
As an inspector- I require a notarized letter from EC stating that the system has been checked or repaired to alleviate the liability on the AHJ. :smile:
celtic said:
What standard accomplishes "checked "?
barbeer said:
I would think that a properly trained, qualified electrician would have the knowledge and tools to effectively accomplish this task. If you positively need a standard (of which I believe there is not a recognized one) try this one.

NFPA 921: Guide for Fire and Explosion Investigations, 2004 Edition

This should help with what to look for- and this one should help with the correct way to repair what needs to be.

National Electrical Code? 2005 Edition (NFPA 70)
I don't need it...YOU do as the inspector that requires the EC to sign off on liability.

While it's comforting to expect a "trained, qualified electrician to effectively accomplish this task", that is not always the case.
If there is not standard that is recognized, what's the point in the notarized letter? Just to cover your OWN posterior? What good does that do the current HO or subsequent HO?

No offense, but this is BS.
 

celtic

Senior Member
Location
NJ
Start with this:

If you require the systems be "checked", create/accept a standard that all can follow equally and that can be enforced fairly.


To simply allow a "notarized letter" as sufficient proof and evidence of "checked" is a joke.

A notary's responsiblity is ONLY that the signature is in fact authenticate ..nothing more. The notary has no duty to see that the facts in the document are true(although a person may have to swear to it), just that the signature is true.

"Checking" a system w/o any sort of standard or enforcement is ludicris. What does "checked" even mean? It's anyone's guess.

Introduce NFPA 921: Guide for Fire and Explosion Investigations, 2004 Edition as the standard...of course, you will need some sort of legislation to have it enacted as law - just like the NEC.
 

celtic

Senior Member
Location
NJ
barbeer said:
As an inspector- I require a notarized letter from EC stating that the system has been checked or repaired to alleviate the liability on the AHJ. :smile:
petersonra said:
and what code requires this?

How'd I miss that?

A very good and valid question.
 
As an inspection authority, it does not take code to require the letter, it may take a policy set forth.

I also agree the letter that Barbeer requests is a little weak. A fire up in the attic seems to me to possibly create water damage in the floors below the attic as well??
 

allenwayne

Senior Member
I had a similar situation a few years ago during a rainy season.Scenario model home got lightning struck.Small attic fire confined to one area.Can lighting and some other branch circuit wiring was burnt.

The F.D. called the building dept.,that called the elec. dept.That immediately had the POCO pull the meter.Resolution was to have a certified engineering firm have the entire homes wiring meggered and any problems fixed then the fix was inspected and then it had to be meggered again.Then all put back in place for a final inspection.The engineering firm made a bundle we did to the real loser was the insurance company.Final bill was somewhere around $40,000.00 when it was all said and done.

No wonder the insurance rates here are so out of reach !!!!!!!!!
 

JohnJ0906

Senior Member
Location
Baltimore, MD
Pierre, I was thinking the same thing while reading this thread. Often there is more water damage than fire damage. How does water affect wiring? How about long term- 20 yrs down the road?
 

brian john

Senior Member
Location
Leesburg, VA
I would think that a properly trained, qualified electrician would have the knowledge and tools

If by this you mean the average service electrician NO WAY, (not slamming anyone just stating the facts as I know them)

What is the issue with megging the circuits, easy enough to do and if there is a problem you might avoid the next fire, saving your home owner from a repeat visit.

In our area we are called to do this all the time (by electrical contractors, contractors, or recommended by engineers and insurance carriers), if the inspector requires a letter, I write the letter, if the inspector needs the letter signed by an engineer I submit a report to an engineer he reviews the documentation and writes his own letter submitting my test documentation and the customer pays a few extra dollars.
 

barbeer

Senior Member
celtic said:
Start with this:

To simply allow a "notarized letter" as sufficient proof and evidence of "checked" is a joke.

I somewhat agree with you! I can not police the EC to make sure he is doing the job he is getting paid for other than my inspection duties. Being in a small town- I am usually at the fire before the owner or insurance co. is in the building so I have some idea of the damage.


celtic said:
What does "checked" even mean? It's anyone's guess.

checked, check?ing, checks

To inspect so as to determine accuracy, quality, or other condition; test: checked the brakes and lights for defects; checked out the system to make sure there were no errors in the software.
To verify by consulting a source or authority: checked her facts before speaking.

Guess no more!

I am just an inspector- someone posted a question and I answered it- whether or not you like the answer I can not help. I am following the existing procedure in my department and as you eluded to earlier getting things adopted or changed is not all that easy, before myself I do not believe my municipality had a true electrician as an electrical inspector - ssoooooooo! Baby steps.
 

hotrod71

Member
water damage

water damage

Pierre C Belarge said:
As an inspection authority, it does not take code to require the letter, it may take a policy set forth.

I also agree the letter that Barbeer requests is a little weak. A fire up in the attic seems to me to possibly create water damage in the floors below the attic as well??

Very little water was put on the fire. It basically only scorched some cellulose insulation and damaged 2 to 3 circuits in a confined area.
 