bhellmer
Member
- Location
- Lee's Summit, MO USA
A customer has select industrial panels that are labeled with an unacceptable SCCR of 5,000 amps. The label does not provide alternative ratings for when fed by current-limiting breakers or fuses.
Of course, I would prefer that different panels with an adequately labeled SCCR be selected. But there is resistance.
We have considered using transformers or inductors to reduce the available-fault current. But first, we want to consider feeding the panels with current-limiting fuses.
UL 508A permits the use of let-through currents when evaluating components on the load side of a current-limiting device protecting the incoming feeder.
I propose feeding these panels with current-limiting Type-J fuses. If re-evaluations according to UL 508A result in SCCRs that exceed the available fault currents, how do I label or otherwise document this re-evaluation and address the manufacturer’s conflicting label. I understand that this re-evaluated SCCR will be non-compliant and void manufactured NRTL listings.
Of course, I would prefer that different panels with an adequately labeled SCCR be selected. But there is resistance.
We have considered using transformers or inductors to reduce the available-fault current. But first, we want to consider feeding the panels with current-limiting fuses.
UL 508A permits the use of let-through currents when evaluating components on the load side of a current-limiting device protecting the incoming feeder.
I propose feeding these panels with current-limiting Type-J fuses. If re-evaluations according to UL 508A result in SCCRs that exceed the available fault currents, how do I label or otherwise document this re-evaluation and address the manufacturer’s conflicting label. I understand that this re-evaluated SCCR will be non-compliant and void manufactured NRTL listings.