What markers are you referring to, tape?
I think they make them for larger conductorsThat looks like it's for small conductors that are inside of a cable. Often those conductors have no markings as the sheath has the required information so using the marker won't violate anything. For larger conductors re-identified with tape utilizing a candy cane stripe should not obscure all of the markings.
You don't need to reidentify the entire exposed length of conductor. Stop marking where the data is.How is re identifying conductors with those markers that re identify conductors code compliant when it covers all the conductor info?
Yup, one circle of tape around the conductor is all that's required. I've seen guys use 1/2 a roll of tape to make it look pretty.You don't need to reidentify the entire exposed length of conductor. Stop marking where the data is.
Other than maybe if you have corner grounded delta and are running the grounded conductor through breakers, contactors, etc. I feel that white tape is a little overkill anyway, if the conductor lands on a neutral bar it is sort of obvious to anyone that knows what they are doing that it is a neutral conductor and that it is nearly always a grounded conductor for NEC applications. I've also said similar about a white conductor with black tape landed on a breaker- 99.99% chance it is not a grounded conductor tape is there for the untrained and even there at least half of them still don't know why the tape is there.One little township inspector ( no state license ) only accepted paint or heat shrink tubing to identify conductors.The NEC should require wires to be marked at least every 12 to 18" in panels. We had over 35 84 circuit panels that were at least 6' high and contractor only marked the grounded conductor with a wrap of cheap white tape that feel off after a few months.
You have a few days left to try to make that change for the 2029 code. The NFPA is accepting Public Inputs for the 2029 code through 5pm Eastern time on April 9th.The NEC should require wires to be marked at least every 12 to 18" in panels.
If its 6 or smaller does it not require the entire conductor to be re-identified?You don't need to reidentify the entire exposed length of conductor. Stop marking where the data is.
I think your allowed to barber pole the entire conductor with tape, or at least you were.IIRC< if it's 6 or smaller you're not allowed to re-identify at all (except for conductors in flexible cords, like turning a white conductor red).
Phase identification you can do about anything you want. where there is more than one voltage system on the premises you do need to post the method used to identify system and phase.IIRC< if it's 6 or smaller you're not allowed to re-identify at all (except for conductors in flexible cords, like turning a white conductor red).