Or pretend you installed it 40 years ago. (Gray and Green were legit colors for ungrounded in the past).
Gray was because of confusion over the wording "natural gray" that used to appear in NEC, though I don't really know that was the intent of the CMP that covers that area of NEC to use gray as an ungrounded conductor and they eventually removed that "natural gray" from the text.
I don't now of green ever being acceptable for ungrounded for anything over 50 volts at least since maybe the 1940's or 1950's. But before then and the beginning of using thermoplastics for insulation, there wasn't much for color variety being used either.
I am more worried about that lamp socket fuse holder and bare EGC connection than the green tape.
No worries, that just powers the shunt trip in this breaker. The bare EGC is part of an NM that runs to the switch in the lobby to kill the main. It was a Boston area thing for many years.
These old buildings used to have outdoor cut out switches, they were often flush mounted down low in the brickwork and accessible from the sidewalk. They directly opened all ungrounded conductors.
I am thinking 1920s-1950s?? Anyway as these buildings had new services installed the old cutouts where abandon but push buttons where installed in the old boxes that shunt tripped the new main.
In the building I took the above picture it was wired to a emergency pull station in the building lobby.
I don't now of green ever being acceptable for ungrounded for anything over 50 volts at least since maybe the 1940's or 1950's. But before then and the beginning of using thermoplastics for insulation, there wasn't much for color variety being used either.
250.119 Identification of Equipment Grounding Conductors.
Unless required elsewhere in this Code, equipment
grounding conductors shall be permitted to be bare,
covered, or insulated. Individually covered or insulated
equipment grounding conductors shall have a continuous
outer finish that is either green or green with one or more
yellow stripes except as permitted in this section.
Green was allowed for ungrounded, and required for EGC, until the 2005 code with its language restricting green or green/yellow stripe for the EGC only.
I had a 2008 code proposal to allow green to be used in traffic signal applications for the green lamp (common practice), it was rejected, but then the CMP had an exception for green in under 50V applications (thermostat wire)
The 2014 NEC added an exception for traffic signal cable, basically what I had proposed, but its a different CMP and chair now.
I don't have an older code book handy, but I think that the older codes required that the EGC be green, but stopped short of prohibiting the use of green for ungrounded conductors.Can you please give a reference to any section in 1987-2002 NEC that allowed green to be anything besides an EGC, for applications above 50 volts. I must have been missing something for several years, or maybe there was some loophole there that was somewhat unnoticed, my guess is the intention was green only be used for EGC.
250.119 Identification of Equipment Grounding Conductors.
Unless required elsewhere in this Code, equipment grounding conductors shall be permitted to be bare,
covered, or insulated. Individually covered or insulated equipment grounding conductors shall have a continuous
outer finish that is either green or green with one or more yellow stripes except as permitted in this section.
This was added in the 2005 NEC: Conductors with insulation or individual covering that is green, green with one or more yellow stripes, or otherwise identified as permitted by this section shall not be used for ungrounded or grounded circuit conductors.
The proposal was by Phil Simmons, author of Soares Grounding..