b_electric
Member
- Location
- Nevada City, CA
- Occupation
- Certified General Electrician
Basically, a commercial 3-phase grid-tied standard system (for the time) was sold and installed in 2015 under 2011 NEC requirements that had no Rapid Shutdown requirements, or 2011 had system-level RSD, I don't remember exactly which cycle it all started which I believe was a shunt-trip at the service, but should be moot for the purposes of this situation, IMHO.
Owner, at some point, removed the system completely to demo the building and build a new building and now wants to re-install old system, and plans reference rapid shutdown requirement in the electrical details that seems more along the lines of 2014 code, but the title sheet references 2017 code (which would require module-level Rapid Shutdown), which, in any case, would be impossible to have rapid shutdown anyway due to the inverters being incompatible with either MLSD modules or using string level devices such, as (non-opti) Tigo's.
owner wants to push re-install of obsolete equipment. I can only suggest re-installing inverters within 10' of the arrays to accommodate the closest thing that could be construed as compliance with rapid shut-down, not that I'd wanna put my name on it or anything... Owner should just bite the bullet and buy new inverters and new string level RSD devices, no? It's a code violation to re-install obsolete equipment, is it not? I don't have my code book available at the moment and could use some honest feedback here, thanks.
Owner, at some point, removed the system completely to demo the building and build a new building and now wants to re-install old system, and plans reference rapid shutdown requirement in the electrical details that seems more along the lines of 2014 code, but the title sheet references 2017 code (which would require module-level Rapid Shutdown), which, in any case, would be impossible to have rapid shutdown anyway due to the inverters being incompatible with either MLSD modules or using string level devices such, as (non-opti) Tigo's.
owner wants to push re-install of obsolete equipment. I can only suggest re-installing inverters within 10' of the arrays to accommodate the closest thing that could be construed as compliance with rapid shut-down, not that I'd wanna put my name on it or anything... Owner should just bite the bullet and buy new inverters and new string level RSD devices, no? It's a code violation to re-install obsolete equipment, is it not? I don't have my code book available at the moment and could use some honest feedback here, thanks.