Sorry Tonyi, I Don?t agree,
The term or heading required outlets wasn?t just thrown into the 2002 addition of the code.
1990 code:
Exception No. 3: In addition to the required receptacles specified by section 210-52, switched receptacles supplied from a general ?purpose branch circuit as defined in section 210-7(a), exception No. 1 shall be permitted.
210-52 in part
(a) General Provisions.
In every kitchen, family room, dinning room, living room, parlor, library, den, sun room, bed room, recreation room, or similar room or area of dwelling units, receptacle outlets shall be installed so that no point along the floor line in any wall space is more than 6 feet measured horizontally, from an outlet in that space,
2002 code
210.52 Dwelling Unit Receptacle Outlets.
(A) General Provisions. In every kitchen, family room, dining room, living room, parlor, library, den, sunroom, bedroom, recreation room, or similar room or area of dwelling units, receptacle outlets shall be installed in accordance with the general provisions specified in 210.52(A)(1) through (A)(3).
1990 code
210-52 (b) small appliance.
(1) the two or more 20-ampere small appliance branch circuits required by Section 220-4(b) shall serve all receptacle outlets, including refrigeration equipment, in the kitchen, pantry, breakfast room , dinning room, or similar area of a dwelling unit. Such circuits, weather two or more are used, shall have no other outlets.
Exception No. 1 A receptacle installed solely for the electrical supply to and support of an electric clock in any room specified above.
(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all receptacle outlets covered by 210.52(A) and (C) and receptacle outlets for refrigeration equipment.
Exception No. 1: In addition to the required receptacles specified by 210.52, switched receptacles supplied from a general-purpose branch circuit as defined in 210.70(A)(1), Exception No. 1, shall be permitted.
Exception No. 2: The receptacle outlet for refrigeration equipment shall be permitted to be supplied from an individual branch circuit rated 15 amperes or greater.
IN both the 1990 code and the 2002 code the exceptions are relevant and necessary if you are going to install a 15-amp circuit serving the wall space in these specified rooms.
Again the current wording only gives allowance for rec on lighting circuits outside of the rec serving wall space and rec serving counters.
That is why it says, shall serve all receptacle outlets covered by 210.52(A){wall space} and (C) {counter Rec.} and receptacle outlets for refrigeration equipment.
[ October 29, 2003, 06:43 AM: Message edited by: david ]