Re: Voltage Drop
Guys, please verify the following VD calculation for #2AWG 13.8KV cable in RMC conduit for 1200feet one way distance. Assume load of 100A.
Cable ampacity for Copper #2AWG 13.8KV is I=145A
R=0.2 from Table 9 of NEC.
by NEC formula, Vd= (1.732xLxRxI)/1000
Vd= (1.732x1200x0.2x100)/1000
= 41.568V
%Vd= 41.568V/13800 = 0.301%