Re: Reactor in Substation
JC
Power line reactors add inductance to lightly loaded HV power lines that are quite capacitive by design. Under little or no load, an HV line, 115KV and above, will sometimes see an increase in the receiving end voltage instead of seeing a drop in voltage over the line. This often happens under lightly loaded conditions, and the reactor will tend to negate the voltage rise.
Also sometimes there are small reactors in individual phases used to block relay communications signals from travelling thru substations and interfering with other signals as well.
Hope that helps
Jim T