Reactors

Grouch1980

Senior Member
Location
New York, NY
I came across these diagrams in an old SPD book by Cooper Bussmann. The section gives examples on how to limit short circuit currents to below that of the AIC ratings of breakers. One example is figure 5-5-12, show below. What is a reactor? And does anyone have any examples or links to a reactor?

IMG_0276 (1).jpg
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Reactors are inductors. They add impedance to the circuit. You don't see them used much in low voltage circuits for scc reduction because they add a lot of vd.

The second diagram is allowed but has to be blessed by UL for the specific combination of fuse and CB being used
 

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
It's just loops of wire with metallic cores that has reactance to help with limiting fault current. It's essentially sort of like an inductor.

Lots of transformer manufacturers make reactors (somewhat similar product except for short circuit current reduction, most use air core rather than solid core).
Personally I have never seen it used in the MEP industry. Have you?
 
Last edited:

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
There are disadvantages to using current limiting reactors to lower the prospective short circuit current (PSCC). One of those is that the reactance of the circuit increases, which lowers the overall power factor and puts a user at risk for PF penalties from the utility unless that then is corrected, such as with PFC capacitors, which can then have other effects on a circuit. It requires very careful engineering to balance these issues out. In other words it’s not a simple cure-all, it’s just one of the potential tools that can be employed when the PSCC ends up exceeding the equipment ratings.

I had to consider it once on an MCC project where the distributor ordered the 2,000A MCC incorrectly to where it was only rated for 42kA and the site was almost 45kA PSCC (we had wanted the MCC to be rated for 65kA). It required getting a PE involved and an expensive air core current limiting reactor that took 10 weeks lead time, but that was less expensive and faster than re-ordering the entire MCC lineup. So like I said, it’s a tool in the kit, but not a cheap or simple one to implement. (We ended up just burying some extra cable to add enough impedance and got it down to 42kA, but that wasn’t cheap either.)
 