There are disadvantages to using current limiting reactors to lower the prospective short circuit current (PSCC). One of those is that the reactance of the circuit increases, which lowers the overall power factor and puts a user at risk for PF penalties from the utility unless that then is corrected, such as with PFC capacitors, which can then have other effects on a circuit. It requires very careful engineering to balance these issues out. In other words it’s not a simple cure-all, it’s just one of the potential tools that can be employed when the PSCC ends up exceeding the equipment ratings.
I had to consider it once on an MCC project where the distributor ordered the 2,000A MCC incorrectly to where it was only rated for 42kA and the site was almost 45kA PSCC (we had wanted the MCC to be rated for 65kA). It required getting a PE involved and an expensive air core current limiting reactor that took 10 weeks lead time, but that was less expensive and faster than re-ordering the entire MCC lineup. So like I said, it’s a tool in the kit, but not a cheap or simple one to implement. (We ended up just burying some extra cable to add enough impedance and got it down to 42kA, but that wasn’t cheap either.)