AKwiring said:This may be a dumb question, but can someone clarify this for me?
If I am measuring the amperage across each leg of a 2 pole 100 amp breaker and one leg reads 60 amps and one reads 50 amps is the service using 55 amps?
or 110 amps?
Can you explain?
Thank you.
AKwiring said:This may be a dumb question, but can someone clarify this for me?
If I am measuring the amperage across each leg of a 2 pole 100 amp breaker and one leg reads 60 amps and one reads 50 amps is the service using 55 amps?
or 110 amps?
Can you explain?
Thank you.
iwire said:A 100 amp breaker in a 120/240 volt single phase panel can supply 24,000 watts (24 KW) evenly balanced.
winnie said:And if that breaker is supplying 60A on one leg and 50A on the other leg, then you have 60*120 + 50*120 = 13200 kva being supplied.
-Jon
480sparky said:Would not 50a on leg B be the same 50a on leg A, the other 10a going back through the neutral?
480sparky said:Would not 50a on leg B be the same 50a on leg A, the other 10a going back through the neutral?
ptonsparky said:Okay, 50A @ 240 = 12000. 10A @ 120 = 1200, for a grand total of 13200.
winnie said:And if that breaker is supplying 60A on one leg and 50A on the other leg, then you have 60*120 + 50*120 = 13200 kva being supplied.
-Jon