Is there a way to find out facility current usage, load current, from utility meter data?
Is there a way to find out facility current usage, load current, from utility meter data?
I did called the utility and they are going to let me know if they have this information, waiting waiting and waiting now.Call the utility. The meter might not display what you are looking for, but they very possibly have historical data they can get you. Peak demand stored in the meter is likely only from the last 30 days. Peak demand during past year will be in the archives at POCO offices though.
In answer to your question though, you cannot determine current from a watt-hour meter. It cannot differentiate 100kWh from being 1kW for 100 hours or 100kW for 1 hour, it all comes out the same to that meter.
this is for a restaurant renovation and I want to find out if existing current usage and additional loads can be handled by the main 600A service.
Here is the picture of the utility meter.
But you should be able to calculate load based on the installed devices in the facility and using a diversity factor.
That's about the best approach, but also consider any seasonal variations that might be involved. If they have A/C, and October is getting cool already, the usage in August might be a lot higher. But what you COULD do is estimate it by looking at your peak current in October, then compare the kWH for August vs kWH in Oct, and use the same differential factor factor to adjust the peak current. So for example Oct. use is 400kWH, August was 700kWh, the differential is 175%. Oct. peak current is 300A, so assume August peak might be as high as 300A x 1.75 = 525A. Not perfect, but better than a total WAG.This is a 4000sqft deli. 3000 sqft of space will be completely renovated 1000sqft of space is remaining the same.
Wiring and the restaurant is about 50 years old. Labels on the electrical kitchen equipment is worn out, no way to tell what is the name plate data is.
Only trustful engineering data I have is 600A service and NEW equipment is 250A.
I was hoping to find out existing current usage.
If utility don't tell me current and demand historical data ,I am planing to rent amp meter and installing it for 30 days.
ConEd said they do not record Amp usage. I said GE meter has the ability to report Amp value, ConEd insisted that they dont record this.
Sent from my SM-G892U using Tapatalk
How would you estimate this;You get the KW value and convert it into amps. Usually people will throw in another bit of fudge on that for less than unity power factor and/or imbalance, but the code doesnt seem to require it. I guess they figure the extra 25% is enough.
How would you estimate this;
1.) 35000kwh avarage electric usage per 30 days
2.) Service cable and ocpd rated 600A.
3.) This is a very busy deli, 4000sq ft.
So how much Amp they are using avarage?
Sent from my SM-G892U using Tapatalk
This:How would you estimate this;
1.) 35000kwh avarage electric usage per 30 days
2.) Service cable and ocpd rated 600A.
3.) This is a very busy deli, 4000sq ft.
So how much Amp they are using avarage?
Sent from my SM-G892U using Tapatalk
Unless customer is subject to demand penalties they might not put demand data on the bill, but they still likely have that data available if you ask for it. Small commercial services, 200 maybe even 400 amp, might not be subject to demand penalties. Larger services may be assessed a demand charge that you pay whether you use what is included in that charge or not. Those also will detail the usage demand.gar gave the answer of how to make an educated guess from this info, but the key is, you need DEMAND in KW not KWH. Demand is the highest average KW usage in a (usually) 15 minute interval. Nearly all commercial customers get demand billing so the utility should be able to furnish this data. It will also be on the power bills if the client has them.