does it feed small wire for a long distance?Looks like some sort of upgrade might be in order soon if this thing went to the top. This is a 4800v line.
I got a picture of the controller dataplate but its too fuzzy to make out. Ill go back with a ladder sometimedoes it feed small wire for a long distance?
it generally works out to .75V per step on a 120V scale, so this one went up 8V
Does your POCO do CVR? (Conservation through voltage regulation).I got a picture of the controller dataplate but its too fuzzy to make out. Ill go back with a ladder sometime. Wow .75V per step, I didnt realize it would be such a small increment.
Im not sure what the wire size is, looks "normal". #2? This is the line that feeds me. Im about 3 miles way from that regulator. Regulator is 6.5 mile from substation, but line starts at 7.62/13.2 and is stepped down to 4800 at mile #5, 1.5 mi from regulator. A GC I work for is the very last customer on the line on one road, about 4.5 miles past me, but the line splits and goes up some other roads and I have never followed those out.
interesting. I was not aware that was a thing. I dont know for sure, but I would guess no for this POCO. at least in my area. what is a typical figure for the percentage that demand can be lowered for a sub by reducing voltage?Does your POCO do CVR? (Conservation through voltage regulation).
we do that through SCADA software at any regulators we have comms with. Line regulators we do not have communication set up with at this time. It’s coming...
when the program is ran, the line regulators step up because there isn't a program telling them to stay low, and they “see” the low voltage, and raise to correct it.
I have limited the raise on some to let the CVR at the station drag the voltage down across the line regulators creating more savings.
On our peaking demand in the winter, our system can see a 50G savings, PER EVENT. Yep, that’s right...interesting. I was not aware that was a thing. I dont know for sure, but I would guess no for this POCO. at least in my area. what is a typical figure for the percentage that demand can be lowered for a sub by reducing voltage?
Got any numbers at all on the data plate? Normally there is a number somewhere like lower right side with data plate number. The data plates are stamped out, and when one is built they ask for the data plate part number to get the correct schematic and P2U2 voltages.
That’s a good pic, it told me everything I needed to know. What else you want to gain from a better picture?This is the best I could do. I could do much better with a 6 foot ladder, its not that high.
That’s a good pic, it told me everything I needed to know. What else you want to gain from a better picture?
are you having voltage issues?
Very cool, thanks for that. I am surprised peak is so early at 7:30. IS that typical?The blue is what we supply from the substation. That peak at the top is CVR benefit, and you can see where the solar is contributing to our load. Not of our better savings day, but it was still helpful.
View attachment 2551862
YepNo just curious. So is it like you though with .75 V per step @ 120? So that means it changes taps every 30V at 4800?
People getting up for work and school, cranking the heat up along with lights, hot water for showers, etc..Very cool, thanks for that. I am surprised peak is so early at 7:30. IS that typical?
Not of our better savings day, but it was still helpful.