I have tenant space which is not guest room or guest suites in third floor of building. All branch circuits are fed from electrical room. The electrical room is maintained by personnel 24 hours. They can call the person to get access to branch circuit.
240.24(B) says each occupant must have ready access to its overcurrent protection devices. Their is not exception for branch circuit if its Not guest suites or guest room.
Would the first paragraph arrangement be call ready accessible or not? I am confused by the definition ready accessible
240.24(B) says each occupant must have ready access to its overcurrent protection devices. Their is not exception for branch circuit if its Not guest suites or guest room.
Would the first paragraph arrangement be call ready accessible or not? I am confused by the definition ready accessible