Pilot Super Grip
Member
- Location
- Non-US
What could be the reason(s) behind the 125% overrating factor required to be applied on conductors and overcurrent devices?
Is it only because UL listed overcurrent devices cannot carry more than 80% of continuous load?
If it is also because a 100% continuous load might not trip the device because of its tripping curve, then how do we explain the exception found in NEC that if the device is listed for operation at 100% of its rating, the ampere rating of the overcurrent device may be equal or greater than the sum of the continuous load plus the noncontinuous load?
Is it only because UL listed overcurrent devices cannot carry more than 80% of continuous load?
If it is also because a 100% continuous load might not trip the device because of its tripping curve, then how do we explain the exception found in NEC that if the device is listed for operation at 100% of its rating, the ampere rating of the overcurrent device may be equal or greater than the sum of the continuous load plus the noncontinuous load?