In the 2008, the rebar in the basement wall will likely be considered a CEE in it's own right, according to the language from the ROC:
Quote:
2008 250.52(A)(3) Concrete-Encased Electrode. An electrode encased by at least 50 mm (2in.) of concrete, located horizontally near the bottom or vertically and within that portion of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 6.0 m 220 ft) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (1/2 in.) in diameter, or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 4 AWG. Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means. Where multiple concrete-encased electrodes are present at a building or structure, it shall be permissible to bond only one into the grounding electrode system.
__________________
I copied this from another thread and had to sleep on it a week or so. Until this morning about 4 am actually.
All basement walls in the area are either tarred of othewise waterproofed, the footings are the only thing that would have direct contact with the earth. On larger commercial jobs you will see rebar extending up from the footing, but not on residential. Will this design exclude using the rebar in walls as a grounding electrode?
Quote:
2008 250.52(A)(3) Concrete-Encased Electrode. An electrode encased by at least 50 mm (2in.) of concrete, located horizontally near the bottom or vertically and within that portion of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 6.0 m 220 ft) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (1/2 in.) in diameter, or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 4 AWG. Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means. Where multiple concrete-encased electrodes are present at a building or structure, it shall be permissible to bond only one into the grounding electrode system.
__________________
I copied this from another thread and had to sleep on it a week or so. Until this morning about 4 am actually.
All basement walls in the area are either tarred of othewise waterproofed, the footings are the only thing that would have direct contact with the earth. On larger commercial jobs you will see rebar extending up from the footing, but not on residential. Will this design exclude using the rebar in walls as a grounding electrode?