Recept. Branch

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
So I questioned someone today on how they drew in branch circuity on drawing. There were about 15 receptacles every 5-6 were on a circuit so he grouped/tied them all together. Basically MWBC. He said he was running 12/6 MC(he says they make it..I've heard of super BX)and each circuit would have a separate neutral. Just from a wiring standpoint wouldn't it be PIA to run 12/6 to first receptacle and splice through? How about box fill? Thanks

Sent from my SM-N960U using Tapatalk
 

david

Senior Member
Location
Pennsylvania
So I questioned someone today on how they drew in branch circuity on drawing. There were about 15 receptacles every 5-6 were on a circuit so he grouped/tied them all together. Basically MWBC. He said he was running 12/6 MC(he says they make it..I've heard of super BX)and each circuit would have a separate neutral. Just from a wiring standpoint wouldn't it be PIA to run 12/6 to first receptacle and splice through? How about box fill? Thanks

Sent from my SM-N960U using Tapatalk

if its 12/6 each circuit having its own neutral than it would not be a multiwire branch circuit.

ill take your word for it that they manufacture the cable, never seen it, if the correct box is used i do not see box fill as an issue
 

mstrlucky74

Senior Member
Location
NJ
if its 12/6 each circuit having its own neutral than it would not be a multiwire branch circuit.

ill take your word for it that they manufacture the cable, never seen it, if the correct box is used i do not see box fill as an issue
Your right about MWBC..my oversight.

Sent from my SM-N960U using Tapatalk
 

WarrMann

Senior Member
Location
Atlanta, GA
I agree, who wants to bring 6 circuits into a receptacle box.
Someone who thinks they're slicker than typical wiring methods. Ive never seen that type of cable in the wild.


3 wire romex costs almost twice as much as 2 wire, i can only imagine what 6 wire romex would cost, let alone 6 wire MC. It's probably priced the same as it's weight in gold.


Sent from my SM-G950U using Tapatalk
 

Johnhall30

Senior Member
Location
New Orleans, LA
Occupation
Engineer
Wouldn't you have to run 10/6 to the first receptacle, because you have 6 conductors in a single raceway? You would have to de-rate the wire by 80%
 

WarrMann

Senior Member
Location
Atlanta, GA
Table 315.10(B)(3)(a) says - "Number of conductors is the total number of conductors in the raceway or cable,"

That's fair, i misspoke. I guess ive just never run into it, as most cables I've used with more than 3 ccc in them were for branch circuits. And 80% of 25 amps is 20, so still no derating required for an outlet branch circuit

Sent from my SM-G950U using Tapatalk
 

Johnhall30

Senior Member
Location
New Orleans, LA
Occupation
Engineer
That's fair, i misspoke. I guess ive just never run into it, as most cables I've used with more than 3 ccc in them were for branch circuits. And 80% of 25 amps is 20, so still no derating required for an outlet branch circuit

Sent from my SM-G950U using Tapatalk

Good point. I did not consider the ampacity of #12 in MC cable to have an ampacity of 25A. However, the ampacity of #12 NM cable is limited to 20A, correct? MC cable can use the ampacity in the 75º column.
 

WarrMann

Senior Member
Location
Atlanta, GA
Good point. I did not consider the ampacity of #12 in MC cable to have an ampacity of 25A. However, the ampacity of #12 NM cable is limited to 20A, correct? MC cable can use the ampacity in the 75º column.
In general, #12 is limited to a 20 amp ocpd per code. (I can't always shoot from the hip with article references)

The 75 degree rating will usually come down to the terminals the wire is terminating into.

Sent from my SM-G950U using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Actually I read it wrong it's 3 circuits with 6 conductors. 6 CCC's derating is 80%.

30*80%=24 amps so the cable is fine with 6 CCC's.
 

mwm1752

Senior Member
Location
Aspen, Colo
I've used multiple conductor MC similar for swamp cooler switch legs - works great - but there was only 1 grounded conductor which would lead into 200.6 for identification of a 12# ga grounded conductor - the 6 conductor would have a properly identified pair neutral with its corresponding ungrounded conductor to be compliant.
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
MC can be ordered in virtually any color configuration. They make MC that is "standard" not stocked but standard that has, for example the colors for what the call a 7 wire furniture whip. 3 hots with shared neutral, 1 hot one neut one green yellow ground and one green ground. for example. But if you want it they will put it up. It may be subject to minimums. My experience is that unless you are in an area where labor rates exceed $60 it is cost prohibitive.
 