what is the min height for the receptacles?
6.5 FORWARD REACH
If the clear floor space only allows forward
approach to an object, the maximum high forward
reach allowed shall be 48 inches (48" = 1219mm)
(See Fig. 6k). The minimum low forward reach is
15 inches (15" = 381mm). If the high forward
reach is over an obstruction, reach and
clearances shall be as shown in Fig. 6l.
6.6 SIDE REACH
If the clear floor space allows parallel approach by
a person in a wheelchair, the maximum high side
reach allowed shall be 54 inches (54" = 1372mm)
and the low side reach shall be no less than nine
inches (9" = 229mm) above the floor (See Fig.
6m). If the side reach is over an obstruction,
reach and clearances shall be as shown in Fig. 6n.
please provide some back up to this.Originally posted by hassaf:
Receptacles does not need to comply with ADA. only devices with oprable parts, such as switches, phone instrument, fire alarm pull stations, etc..
Does this mean that the employer refuses to hire disabled employees? Or does this mean that only able-bodied people are allowed to enter the premises?Originally posted by hassaf:
Receptacles does not need to comply with ADA. only devices with oprable parts, such as switches, phone instrument, fire alarm pull stations, etc..
As stupid as it may sound, I would say yes, they do. Here it what Section 1108.13 of the 2000 IBC says (sorry, I don't have the 2003 here).Originally posted by roger:
Does this include "placebo" thermostats?
Roger
So, these placebo thermostats are installed with the intent of the occupant using them, correct? I mean, even though they serve no function, could there be a lawsuit?1108.13 Controls, operating mechanisms and hardware:
Controls, operating mechanisms and hardware intended for use by the occupant, including switches that control lighting and ventilation, and electrical convience outlets, in accessible spaces, along accessible routes or as part of accessible elements shall be accessible.
well it would be easy to move, the wiring wouldn't be difficult.Do I remodel and put his thermostat down to 48" or do I fire him?