Recept transition

Status
Not open for further replies.

wireday

Senior Member
Location
New England
Occupation
Master electrician
Am I ok to transition from a flush in wall receptacle to LFMC , I would like to remove the receptacle install stainless plate with 1/2 inch knockout for the flex.
 
Nothing prohibiting it and if I needed to do it for some reason I would.
 
My memory suggest this method will require an EGC, if the cover was loose the bonding path is lost with no egc
 
This is done all of the time to power office furniture partitions. As Tom stated an EGC is required so that you're not relying on the plate screws to carry the EGC current during a fault.
 