Recept transition

Status
Not open for further replies.

wireday

Senior Member
Location
New England
Occupation
Master electrician
Am I ok to transition from a flush in wall receptacle to LFMC , I would like to remove the receptacle install stainless plate with 1/2 inch knockout for the flex.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Nothing prohibiting it and if I needed to do it for some reason I would.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
My memory suggest this method will require an EGC, if the cover was loose the bonding path is lost with no egc
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This is done all of the time to power office furniture partitions. As Tom stated an EGC is required so that you're not relying on the plate screws to carry the EGC current during a fault.
 