So there is nothing in the code book that requires that you need any receptacles in churches, commercial building, hotels motels or warehouses?:confused:
 

wirebender

Senior Member
210.63 does not require 20 amp receptacles, they can be 15 amp.


It actually doesn't require any receptacles unless there is heating, air conditioning,and refrigeration equipment.:grin:
 

Volta

Senior Member
Location
Columbus, Ohio
And might need some for show windows, not necessarilly 20 amp, unless one will supply more than 7.5 feet of window width if considered a continuous load, or 9 feet if not. 210.20(A), 210.62 and 220.14(G)(2), depending on this and that.
 

Smart $

Esteemed Member
Location
Ohio
So there is nothing in the code book that requires that you need any receptacles in churches, commercial building...?:confused:

210.50(B) Cord Connections. A receptacle outlet shall be installed wherever flexible cord with attachment plugs are used. Where flexible cords are permitted to be permanently connected, receptacles shall be permitted to be omitted for such connections.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
The NEC does not require any receptacles in a commerical building, but those that are installed are counted as part of the connected load at 180 VA each.
In a dwelling unit, receptacles are required, under the 6 ft rule, but all the receptacles are counted in the 3 VA/Sq Ft. IE in dwelling unit you can have an unlimited number of receptacles.
 