can a receptacle be installed above a drop ceiling for cord and plug condensate pump, 120 volt 1.6 amps
yes it isIs it a plenum?
is there a code article that we can not have receptacle in the ceiling I've looked in the code book and haven't find an article that says I cantI've seen it done a lot and have done a few. You need a pump with a plenum rated cord.
There is an old thread http://forums.mikeholt.com/showthread.php?t=124072
is there a cord article that we can not have receptacle in the ceiling I've looked in the code book and haven't find an article that says I cant
thanks I appreciatedNothing prohibits a receptacle above the ceiling.
400.12 prohibits a flexible cord or cable above the ceiling.
Nothing prohibits a receptacle above the ceiling.
400.12 prohibits a flexible cord or cable above the ceiling.
See if the hvac guy can get a direct wired condensate pumpcan a receptacle be installed above a drop ceiling for cord and plug condensate pump, 120 volt 1.6 amps
Yup, receptacle permitted not the cord. Dumb IMO.
I thought the latest that Mike Holt's been preaching is that cords that are part of an appliance are under a different ANSI standard and were not subject to the provisions in the code not allowing flexible cords above drop ceilings?
I've never heard that do you have a reference?
Sorry I guess it was a UL listing thing, taken from a thread back in 2014. About cords and receptacles above drop ceiling.
Originally Posted by jtinge![]()
Just reviewing a few past threads regarding receptacles above suspended ceilings, which everyone seems to agree is permitted. However, there was a consensus opinion that they couldn't be used for anything other than temporary power for tools BECAUSE 400.8 did not permit flexible cords above a suspended ceiling.
Then there was a pretty lengthy discussion ("cords" above ceiling) about whether a power cord for a TV, projector, etc is in fact a flexible cord covered by the prohibitions in NEC 400.8. The arguement being that power cords are UL listed differently than flexible cords and thus not prohibited above suspended ceilings. After 105 thread responses, I'm not sure there was any resolution to the debate.
Clarifying this issue sure would go far into the discussion about whether or not you can plug a ceiling mounted projector to an above ceiling receptacle.
Does anyone have any further insight into this conundrum and whether or not there is any code activity to clarify the issue?
Mike Holts position is power supply cords have a different listing than portable cords and the power cords are allowed.
Attached Images![]()
![]()
I thought the latest that Mike Holt's been preaching is that cords that are part of an appliance are under a different ANSI standard and were not subject to the provisions in the code not allowing flexible cords above drop ceilings?
There was a video about it but don't remember the link. Might be able to find it on MH's YouTube page.