receptacle above electric baseboard heater- NEC year?

Status
Not open for further replies.

itisdillon

Member
Location
NJ/NY
Occupation
QA
In what year did the NEC prohibit a receptacle above an electric baseboard heater? I'm having trouble finding this via Google.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The nec is quiet on the subject. It has always been the manufacturers instructions that prohibited receptacles installed above electric baseboard heat
 

dkidd

Senior Member
Location
here
Occupation
PE
II. Installation

424.9 General. All fixed electric space-heating equipment
shall be installed in an approved manner.
Permanently installed electric baseboard heaters equipped
with factory-installed receptacle outlets, or outlets provided as
a separate listed assembly, shall be permitted in lieu of a receptacle
outlet(s) that is required by 210.S0(B). Such receptacle
outlets shall not be connected to the heater circuits.

Informational Note: Listed baseboard heaters include instructions
that may not permit their installation below receptacle
outlets.
 