From what I remember a while back, receptacles are allowed above a hung ceiling and in particular a receptacle above a hung ceiling is OK for a ceiling mounted projector. I'm reading an article from EC&M about "The best of the worst: 2019's most interesting what's wrong here photos" and one of the slides is on receptacles above hung ceiling.
It says:
"Suspended ceilings can sometimes contain hidden violations such as these power supply cords. The power supply cords are supplying power to a ceiling-mounted projector and its associated equipment, which are located a few ceiling tiles away from these receptacles. Installing receptacles above a suspended ceiling is not prohibited by the NEC. However, leaving power supply cords permanently plugged in and hidden above the suspended ceiling is a violation of Sec. 400.12(5). This rule prohibits flexible cables, flexible cord sets, and power supply cords from being concealed in walls, floors, or ceilings — and also prohibits them from being located above a suspended or dropped ceiling. The exception for Sec. 400.12(5) permits flexible cables and cords to be installed above this suspended ceiling where they are installed in an enclosure specifically designed to be installed in plenum-type suspended ceilings, as permitted by Sec. 300.22(C)(3)."
I tried looking up section 400.12(5) in the 2014 NEC but it looks like it's from the newer 2017 code. But based upon this, anything permanently plugged into a receptacle above a hung ceiling is not allowed??
Has this always been the case or is this requirement new?
It says:
"Suspended ceilings can sometimes contain hidden violations such as these power supply cords. The power supply cords are supplying power to a ceiling-mounted projector and its associated equipment, which are located a few ceiling tiles away from these receptacles. Installing receptacles above a suspended ceiling is not prohibited by the NEC. However, leaving power supply cords permanently plugged in and hidden above the suspended ceiling is a violation of Sec. 400.12(5). This rule prohibits flexible cables, flexible cord sets, and power supply cords from being concealed in walls, floors, or ceilings — and also prohibits them from being located above a suspended or dropped ceiling. The exception for Sec. 400.12(5) permits flexible cables and cords to be installed above this suspended ceiling where they are installed in an enclosure specifically designed to be installed in plenum-type suspended ceilings, as permitted by Sec. 300.22(C)(3)."
I tried looking up section 400.12(5) in the 2014 NEC but it looks like it's from the newer 2017 code. But based upon this, anything permanently plugged into a receptacle above a hung ceiling is not allowed??
Has this always been the case or is this requirement new?