So now comes the question, could this receptacle located 78 inches off the floor be considered as serving the counter top.(6) Kitchens ? where the receptacles are installed to serve the countertop surfaces
In conclusion I would say that if the countertops are 58 inches off finish floor then this receptacle will be required to be GFCI protected.(5) Receptacle Outlet Location. Receptacle outlets shall be located above, but not more than 500 mm (20 in.) above, the countertop. Receptacle outlets rendered not readily accessible by appliances fastened in place, appliance garages, sinks, or rangetops as covered in 210.52(C)(1), Exception, or appliances occupying dedicated space shall not be considered as these required outlets.