What code section would you cite to disapprove this?
What code section would you cite to disapprove this?
As I stated I don't go with me either. Just stating how the NEC reads to me. My problem is when you have a tub surround and there is 2 or 3' from the wall to the tub edge. Why would that not be compliant when the receptacles can be 2" off the edge of the tub over that vanity.This is were the designer showed it!
I frankly go with the Shower or Tub and it's tiles are a footprint of said subject, IE breaking a plain there of, off the tub edge this foorprint would be straight up from the edge.
I can't go with you Dennis.
I realize that this topic has been beat around for some time (especially with respect to interpretation of the definitions); however, here is 1 more photo to add to the collection. My opinion is that this should not have been approved (home is ca. 2005). Just looking for more opinions. View attachment 7783
IMO, it does say it cannot be installed where it is located in the pic. It says "within or directly over a bathtub or shower stall". The key word here is stall. The words bathtub and shower only serve to limit the type of stall. IMO, the receptacle is within the bathtub stall.Now we can use Charlie's words if you want and you can say that 406.9(C) does not state that the receptacle cannot be installed where located in the pic because that is not directly over the tub and it is not within the tub space.
So by what criteria do we establish what is and isn't a stall....??? :slaphead:Suppose that wall was 3' back? 2' back ?????
IMO, it does say it cannot be installed where it is located in the pic. It says "within or directly over a bathtub or shower stall". The key word here is stall. The words bathtub and shower only serve to limit the type of stall. IMO, the receptacle is within the bathtub stall.
So by what criteria do we establish what is and isn't a stall....??? :slaphead:
IMO, it does say it cannot be installed where it is located in the pic. It says "within or directly over a bathtub or shower stall". The key word here is stall. The words bathtub and shower only serve to limit the type of stall. IMO, the receptacle is within the bathtub stall.
So by what criteria do we establish what is and isn't a stall....??? :slaphead:
I think it cleary says within or over the stall. What isn't clear is how we determine what is or isn't a stall? In most cases, it's not hard to determine. But I can imagine some that would be.. just as I know you can.And my opinion is that it does not clearly say this. Is the wall a bathtub or shower stall?
I can see your perspective and cannot discredit it.How many times, if ever, have you heard the term "bathtub stall"?
IMO, the description is for two different items, either a bathtub, or a shower stall. I don't think they meant "bathtub stall" or "shower stall". I think they mean just what it says, a bathtub (stop) or shower stall.
That was exactly my point earlier. In the tub or over the tub- on the ceiling. I cannot even guess the intent here.I can see your perspective and cannot discredit it.
However, if we go with your interpretation, the requirement reduces to "Receptacles shall not be installed within a bathtub."
Hmmm... :slaphead:
I can see your perspective and cannot discredit it.
However, if we go with your interpretation, the requirement reduces to "Receptacles shall not be installed within a bathtub."
Hmmm... :slaphead:
1999 NEC 550-8(b)No receptacle shall be required in the area occupied by a toilet, shower, tub, or any combination thereof. If a receptacle is installed in such an area, it shall have ground-fault circuit-interrupter protection for personnel.
Forgive me for using your post to make a point, but it is applicable. This exemplifies the ridiculousness of the NEC.I will assume the recptacle is on the right side of the stud. Move it to the left side & you are
good. You could move it to the next stud to the left however that puts the recptacle in the
mirror. They do cut holes in the mirror for this situation.