K karn Senior Member Location United States Occupation Electrician Oct 16, 2017 #1 Print calls for a GFCI receptacle to be mounted to the interior of this cabinet, are there any clearance issues with this?
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer Oct 16, 2017 #2 I don't include receptacles in the category of equipment that might require maintenance (or other activities on the list) while energized. So I don't believe the clearance requirements of 110.26 apply.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Oct 16, 2017 #3 GFCI are required to be readily accessible.
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer Oct 16, 2017 #4 I think this installation would be readily accessible. All you have to do is open the cabinet door.