Hi all,
I have a simple question as my first of many posts here on this forum. I am designing a small coffee vendor area for a university. It will have a vertical display case that draws 16.5A. The product uses a NEMA 5-20P. Does this mean that the receptacle should be 5-20R?
Table 210.21(B)(2) in the 2014 NEC states that the max load for a 20A receptacle is 16A. I think that I should size the receptacle and breaker larger to follow NEC, but I would like some other input. Information about the display case is here: http://www.turboairinc.com/index.php/tom-48-dx.html
Thank you!
I have a simple question as my first of many posts here on this forum. I am designing a small coffee vendor area for a university. It will have a vertical display case that draws 16.5A. The product uses a NEMA 5-20P. Does this mean that the receptacle should be 5-20R?
Table 210.21(B)(2) in the 2014 NEC states that the max load for a 20A receptacle is 16A. I think that I should size the receptacle and breaker larger to follow NEC, but I would like some other input. Information about the display case is here: http://www.turboairinc.com/index.php/tom-48-dx.html
Thank you!