Hello,
I want to verify the grounding of a receptacle in a commercial application. The receptacle is to be installed in a metal 4X4 box with a metal cover. The raceway is EMT. It looks like, in the NEC, that the EMT can be used as the the ground and all I need is a bonding jumper from the receptacle grounding terminal to the metal box. It would seem to me that if the integrity of the EMT where ever violated then, a separate grounding conductor should be used. I think I like the idea of both a bonding jumper and a separate grounding conductor but I would like to know the NEC requirement.
I want to verify the grounding of a receptacle in a commercial application. The receptacle is to be installed in a metal 4X4 box with a metal cover. The raceway is EMT. It looks like, in the NEC, that the EMT can be used as the the ground and all I need is a bonding jumper from the receptacle grounding terminal to the metal box. It would seem to me that if the integrity of the EMT where ever violated then, a separate grounding conductor should be used. I think I like the idea of both a bonding jumper and a separate grounding conductor but I would like to know the NEC requirement.