So I met with a customer the other day that had some outlets in the kitchen not working. As I removed the gfci receptacle I noticed that the neutral was bonded to the ground. After talking with the homeowner I found out he had just purchased the house and one of the items on the contract was that the sellers had to ground all the receptacles. Evidently they got some hack in there to basically fake the home inspector into thinking that they were grounded. I guess they should have figured that out when it only cost $65 for the guy to ground them:thumbsdown: We went through the entire house and all the receptacles were wired this way. My thought was to just run a ground wire from each receptacle but after talking with AHJ he informed me that if he had to get involved he would not be able to pass that. So, basically we would have to rewire all the receptacles back to the panel which is fine by me $$$$$
I was just curious about this and wanted some feedback. Thanks in advance.