I would say no,Originally posted by georgem:
If the EGC is connected to the green screw of a "self-grounding" receptacle, is the bonding through the brass clip and steel screw of the yoke to the metal box sufficient to constitute bonding to the metal box?
250.148 Continuity and Attachment of Equipment Grounding Conductors to Boxes.
The arrangement of grounding connections shall be such that the disconnection or the removal of a receptacle, luminaire (fixture), or other device fed from the box will not interfere with or interrupt the grounding continuity.
I do not know of any article that lets a device ground the box it is mounted to.250.146(A)Surface Mounted Box.
Where the box is mounted on the surface, direct metal-to-metal contact between the device yoke and the box shall be permitted to ground the receptacle to the box. This provision shall not apply to cover-mounted receptacles unless the box and cover combination are listed as providing satisfactory ground continuity between the box and the receptacle.