517.30(E) is not giving any specific colour identification of receptacles for different branches of normal and essential electrical system.
Any idea??



Sent from my iPhone using Tapatalk
 
In most cases it is red but it can be any color other than what is used for the Normal Branch receptacles as long as it is standardized through out the facility.

Roger
 
No soecific requirements except for local changes.


In Washington a state NEC amendment requires orange for emergency power, including receptacles.
 