When i start studying load calculation for a single dwelling unit in a apartment,i found general receptacles loads (180VA/receptacle)in living and common area are not included.Is it true ?
 
Re: Receptacle load

No, general purpose receptacles are included in the general lighting load for all dwelling occupancies. See 220.14(J)
 